Hvac

Who is the heat and air guru
I have a rheem classic 90 about 4 years old
started in the spring thought it was low on propane
but is still doing it this fall
will cycle and heat like it should then cycle off
next time it will cycle blower will kick on
cycle back off b/4 it should, kinda like it runs out o propane ?
will cycle on off on off on off several times
without lighting, will go in shutdown mode... I guess is what it would be called
10- 15 minutes later will go thru the same ****
sometimes it will light and run sometimes it wont

thermostat cause this?
HELP..
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 10-24-2008, 07:21 PM   #2
wilson1010
 
Join Date: Feb 2007
Posts: 147
thermocouple
__________________
Unimog 406
XJ with a bunch of stuff put on by somebody else
wilson1010 is offline   Reply With Quote
Old 10-24-2008, 07:25 PM   #3
JeffK5
Tiny Member
 
JeffK5's Avatar
 
Join Date: Jan 2007
Location: Colerain
Posts: 798
Quote:
Originally Posted by wilson1010 View Post
thermocouple

Bingo!

Had my NG furnace do the same thing ....
JeffK5 is offline   Reply With Quote
Old 10-24-2008, 09:04 PM   #4
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
thremowho?
these hard to replace ?
where to buy?
guess i need model # and name of furnace
cost much?
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 10-25-2008, 12:34 AM   #5
itbrokeagain
Just Empty Every Pocket
- CORE Member -
 
itbrokeagain's Avatar
 
Join Date: Feb 2007
Location: Amelia
Posts: 1,435
Send a message via AIM to itbrokeagain
616 5750 Mike sawyer.
__________________
91 fj 80 on 37 Nitto Muds with a 10k winch. Cage and sliders coming soon.
itbrokeagain is offline   Reply With Quote
Old 10-25-2008, 12:50 AM   #6
carwash
pimpin' IS easy
 
Join Date: Jan 2007
Location: Union, KY
Posts: 3,344
Images: 605
Send a message via AIM to carwash Send a message via Yahoo to carwash
same thing happened to ours this past spring to end the season. replaced the whole thing... not sure if the thermocouple is hard or expensive, we just needed a new furnace and didnt want to dump any money into the old one.
__________________


carwash is offline   Reply With Quote
Old 10-25-2008, 10:25 AM   #7
JeffK5
Tiny Member
 
JeffK5's Avatar
 
Join Date: Jan 2007
Location: Colerain
Posts: 798
A thermocouple is nothing more than temp. probe that sends info to the "brain" in your furnace.

When it acts up it gives the units controller bogus information , the problem my furnace had was it thought the fire on the burner failed to light so it shut the gas off ...even though the fire was burning as it should.

Turns out the thermocouple had shorted internally and was not sensing any heat ... no signal from the TC to tell it "successful ignition" so it shuts down.

Cheap and easy!
JeffK5 is offline   Reply With Quote
Old 10-25-2008, 03:19 PM   #8
nick
wheeler
 
Join Date: Jun 2008
Location: owingsville ky
Posts: 25
your furnace should have a flashing light on the control board count the number of blink through the door do not take blower door off it will reset the board and you will have to wait for it to do it again on the door somewhere there should be a list of numbers that will give you the definition of what the blinks mean.. a 90% furnace does not have a thermo couple it has a flame sensor my guess is the furnace is getting to hot check your filters
nick is offline   Reply With Quote
Old 10-26-2008, 02:37 PM   #9
RuffedUpXJ
On XJ 2 Now
 
RuffedUpXJ's Avatar
 
Join Date: Feb 2007
Location: Fairfield Twp.
Posts: 314
Send a message via AIM to RuffedUpXJ
Mine actually started acting up and it was due to the pressure switch which tells the control board the exhaust fan for the fumes is working. I did read my basically CEL on the board and thats what came up and I jumped it for now so the control board believes the switch is sensing the exhaust fan is working but Monday I am getting the switch so I don't need to jump it every time I want to heat my house it.

Basically the way your furnace will work is the exhaust fan will turn on first and it hopefully works and then the pressure switch tells the board everything is good. Then the hot surface igniter kicks on and glows. Then the gas control valve kicks on and starts the gas flow which goes through your plenums. The gas is ignited and the flame sensor send a voltage to the control board saying there is a flame. Sometimes the FS goes bad and you need to replace it ($30). So mine would cycle and start and reach a flame but after about 5 seconds of igniting the gas it would kick of because the exhaust weren't be sensed as leaving the chamber. But there should be a little plastic lens so you can see your control board with the lower cover on. Once it messes up and doesn't continue to run watch to see if the LED blinks. If it does take the cover off and read the panel which should tell you what might be wrong.

Hopefully that helps a little.
__________________
88 XJ - 5" lift - 35" BFG's - Bumpers - Rock Rails - Homebrewed OBA - Roof Rack - Tube Doors - Trimmed - Dented

87 XJ - D44 - Disco D30 - 235's - 231TC - Stock for now
RuffedUpXJ is offline   Reply With Quote
Old 10-26-2008, 04:56 PM   #10
itbrokeagain
Just Empty Every Pocket
- CORE Member -
 
itbrokeagain's Avatar
 
Join Date: Feb 2007
Location: Amelia
Posts: 1,435
Send a message via AIM to itbrokeagain
Little trick. Take some fine grit sand paper to the flame sensing rod. These get all carboned up and dont sense the heat properly. On a 90% Rheem Im guessing its a spark ignition and if its like the waterheaters, the spark ignitor is also the flame sensor.
__________________
91 fj 80 on 37 Nitto Muds with a 10k winch. Cage and sliders coming soon.
itbrokeagain is offline   Reply With Quote
Old 10-27-2008, 12:14 AM   #11
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
took the covers off
kinda dusty, 1 filter wasnt put in correctly
since i cleaned them last...what a dumb ass
anyway vacuumed the area
found what appears to be a round springy switch thing
about the size of a quarter
cleaned it real good wiped it off with finger
wiped something else down... inch or two long
about 1/4 inch round
anyway ducked the safety switch down
like anyone would and fired it up
went thru a cycle just fine
12 hours later
is still working fine
hopefully it is fixed
thanks guys
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 10-28-2008, 03:35 PM   #12
pete
 
Join Date: Mar 2008
Location: sharonville
Posts: 26
did anyone fess up that they were a hvac guy. I need a furnace installed.have the furnace just dont have duct work yet. let me know if anybody does this cheap lol thanks pete
pete is offline   Reply With Quote
Old 10-29-2008, 01:56 PM   #13
itbrokeagain
Just Empty Every Pocket
- CORE Member -
 
itbrokeagain's Avatar
 
Join Date: Feb 2007
Location: Amelia
Posts: 1,435
Send a message via AIM to itbrokeagain
Quote:
Originally Posted by pete View Post
did anyone fess up that they were a hvac guy. I need a furnace installed.have the furnace just dont have duct work yet. let me know if anybody does this cheap lol thanks pete
Quote:
Originally Posted by itbrokeagain View Post
616 5750 Mike sawyer.
:)
__________________
91 fj 80 on 37 Nitto Muds with a 10k winch. Cage and sliders coming soon.
itbrokeagain is offline   Reply With Quote
Old 10-29-2008, 03:45 PM   #14
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
yep, seems to still be still working
the way it should
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 11-09-2008, 12:35 AM   #15
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
furnace isn't fixed, it is just messin with my head
well at least it's not periodic, doesn't work at all now
took what appears to be the flame sensor out
sanded, put it back in.
has LED's... flashes 4 times then starts what i think is a new cycle
doesn't even get to the ignition stage at all
pressure switch maybe.
looks like the yellow pages on this
not sure what else to do here
Called the # above but hate 2 keep aggrivating to guy
is a far drive for him
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 11-09-2008, 12:19 PM   #16
itbrokeagain
Just Empty Every Pocket
- CORE Member -
 
itbrokeagain's Avatar
 
Join Date: Feb 2007
Location: Amelia
Posts: 1,435
Send a message via AIM to itbrokeagain
Hmmmm I thought he lived around here.
__________________
91 fj 80 on 37 Nitto Muds with a 10k winch. Cage and sliders coming soon.
itbrokeagain is offline   Reply With Quote
Old 11-09-2008, 05:41 PM   #17
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
said he lived in harrison
jacked with the pressure switch
seems to be working, getting correct volts anyway
started jacking with thermostat and it started working again
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 11-10-2008, 04:46 PM   #18
yellowjacket
barely breathing
 
yellowjacket's Avatar
 
Join Date: Mar 2008
Location: alexandria, ky
Posts: 889
hvac dude here. back of your furnace doooor should have a chart what those codes mean. if it is your pressure switch not making, check 2 things. when your furnace is tying to light but failing, take your front combustion air (burner) door off. if it lights now, that means youve got a restiction in the intake pipe. leave, birds nest, ect. dosent light? try to clean your trap. if your furnace is a 90% or more, youll have tubes going down from below the inducer motor to a cannister(trap) before out to the drain. take it off and flush it in the sink. make sure you have it primed with water upon reinstall. hope it helps, rob. ive got to pm you about some other stuff, anyway. rob
yellowjacket is offline   Reply With Quote
Old 11-13-2008, 11:21 PM   #19
cincygman
 
Join Date: Nov 2008
Location: Pleasant Run Farms (near Fairfield)
Posts: 378
Is the furnace fixed yet? You can't leave a guy hanging....................
__________________
Romans 7-8
cincygman is offline   Reply With Quote
Old 11-14-2008, 12:18 PM   #20
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
lol...
yep is/was the POS thermostat
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Old 11-15-2008, 12:15 AM   #21
cincygman
 
Join Date: Nov 2008
Location: Pleasant Run Farms (near Fairfield)
Posts: 378
OK, just had to know. By the way I'm also a tech if Yellowjacket isn't around.
__________________
Romans 7-8
cincygman is offline   Reply With Quote
Old 11-15-2008, 01:39 AM   #22
fabricator
 
fabricator's Avatar
 
Join Date: Jan 2007
Location: Cincy, Oh
Posts: 947
I appreciate the help
lord knows i need it
__________________
For you guys who can't drive, I have owned a frame rack for several years. Prices are based on your skill and ability to wreck it....
fabricator is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 08:33 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Copyright 2021, C.O.R.E. All rights reserved.